SAP for Utilities Discussions
Connect with fellow SAP users to share best practices, troubleshoot challenges, and collaborate on building a sustainable energy future. Join the discussion.
cancel
Showing results for 
Search instead for 
Did you mean: 

What is Transformer Factor?

Former Member
0 Kudos

Hi,

Can anyone explain me the difference between Transformer Factor and Transformation ration and how it is caliculated in SAP?

Regards,

Bankim.

2 REPLIES 2

murtuza_chhatariya
Active Participant
0 Kudos

Hi,

Please go through below thread

[;

Thanks,

Murtuza

former_member421468
Participant
0 Kudos

Hi,

K-factor is a weighting of the harmonic load currents according to their effects on transformer heating, as derived from ANSI/IEEE C57.110. A K-factor of 1.0 indicates a linear load (no harmonics). The higher the K-factor, the greater the harmonic heating effects

The K-Factor is used by transformer manufacturers and their customers to adjust the load rating as a function of the harmonic currents caused by the load(s).

Transformation ratio is the ratio of:

secondary voltage/primary voltage OR

secondary winding/primary winding OR

primary current/Secondary current

Thanks,

Harshal