Modbus driver support for SAP MII

0 Kudos

The I/O device from which the data needs to be fetched implements a Modbus protocol on its serial ports.

Does SAP MII have Modbus driver support for connector which can poll or query the I/O device to fetch data from it? or Is there any connector which can directly poll the the I/O device implementing Modbus protocol?

Accepted Solutions (1)

Accepted Solutions (1)

former_member196557
Active Contributor
0 Kudos

Use an OPC Server such as KepWare with the Modbus Serial Driver, and access the OPC tag data through PCo (V2.1) or UDS, recommend PCo 2.1 if possible. You can find info about the Kepware product and pricing at

http://www.kepware.com

- Steve

Answers (1)

Answers (1)

Former Member
0 Kudos

Adding to Steve's reply, you need to procure a hardware which converts Modbus to TCP/IP converter as well. Please check the following link for Modbus Gateways.

http://www.moxa.com/land/mhq-en/dn-fieldbus-gateway/?_kk=modbus&_kt=b15ee80e-f7b0-4367-9305-00e144dc...

Combination of Kepware Modbus OPC server and Modbus Gateway will provide you a way to access from MII

0 Kudos

I understand that Modbus driver coming along with the OPC server does take care of the conversion from Modbus to TCP / IP conversion?

In that case is the hardware for conversion required?

former_member196557
Active Contributor
0 Kudos

Modbus Serial and Modbus TCP are slightly different protocols. In order to use Modbus Serial with an OPC Server, the server must be able to access a COM port on the server where the OPC Server is running, and the COM port is then connected to the Modbus Serial Device. In order to use Modbus TCP, the Modbus Serial device must be physically connected to a protocol converter that can convet Modbus Serial to Modbus TCP/IP; this device in turn is connected to a network that the OPC server can access to connect to the Modbus TCP device. Alternately, there some Ethernet to serial adapters that offer a virtual COM port driver such that the connect looks like this:

ModbusSerialDevice<serial>SerialtoEthernetAdapter<-TCP/IP>VirtualComPortDriver<-COM Port Access>Modbus Serial OPC Server.

Either one will work. The advantage to using the ModBus TCP adapter is that it can be connected to by more than one OPC Server if necessary.

- Steve

0 Kudos

Thanks

Just reframing my original question.

Is there any connector in SAP MII (or inbuilt Modbus support) where we can directly fetch the data from the Modbus compliant device without using an Modbus OPC server?

former_member196557
Active Contributor
0 Kudos

None that I am aware of.

Here is the link to the Modbus site, there are a lot of technical resources available for you to investigate if you want to develop a communication driver yourself: [www.Modbus.org|http://www.modbus.org].

- Steve